SIMULATION - A recent power outage caused email services to go down. A server administrator also received averts from the datacenter's UPS. After some investigation, the server administrator learned that each PDU was rated at a maximum of 12A. Instructions - Ensure power redundancy is implemented throughout each rack and UPS alarms are resolved. Ensure the maximum potential PDU consumption does not exceed 80% (or 9.6A). a. PDU selections must be changed using the penal icon. b. VM Hosts 1 and 2 and Mall Relay can be moved between racks. c. Certain devices contain additional details. If at any time you would like to bring back the initial state of the simulation, please click the Reset All button.![]()
![]()
![]()
![]()
![]()
![]()
![]()
![]()
![]()
![]()
![]()
![]()
 Suggested Answer: See explanation below. 1. Mailrelay - Keep the mail relay on the existing Rack1 and change the primary power supply to PDU-B and Failover powersupply as PDU B. 2. Move the VM Host 1 and VM Host2 to Rack2. Assign primary power supply PDU A to VM host1 Assign Failover power supply PDU B to VM host1 Assign primary power supply PDU B to VM host2 Assign Failover power supply PDU A to VM host2 This question is in SK0-005 CompTIA Server+ Exam For getting CompTIA Server+ Certificate Disclaimers: The website is not related to, affiliated with, endorsed or authorized by CompTIA. Trademarks, certification & product names are used for reference only and belong to CompTIA. The website does not contain actual questions and answers from CompTIA's Certification Exams.